If the power goes out in the building for any reason, the gym door will lock automatically. It's an electronic lock with no manual override so if the power were to go out while I was in the gym, I'd be stuck there, in the dark, until the power came back on. That's a scary thought! There's no phone in the gym and I don't get cell reception in there either, so no calling for help. Another worry is what if I hurt myself or pass out or something while I'm in the gym - I'd either have to crawl to safety or wait for someone to notice me - again, no ability to phone for help.
Cat - this is something that is most probably against the Wisconson Public Safety Code - which references the Life Safety Code (NFPA 101) 7.2.1.6.2 - Access controlled
Egress Doors. Where permitted in Chapters 11 through 42 (39 addresses Business occupancies, 42 is Storage).....doors in the means of egress shall be permitted to be equipped with an approved entrance and egress access control system, provided that the following criteria are met.
(a) - a sensor shall be provided on the egress side and arranged to detect an occupant approaching the doors, and the doors shall be arranged to unlock in the direction of egress upon detection of an approaching occupant
or loss of power to the sensor.
(b) - loss of power to the part of the acdcess control system that locks the doors shall automatically unlock the doors in the direction of egress.
(c) the doors shall be arranged to unlock in the direction of egress from a manual release device located 40 inches to 48 inches vertically above the floor and within 5 feet of the secured doors. The manual release device shall be readily accessible and clearly identified by a sign.......
(d) activation of the building fire-protective signalling system shall automatically unlock the doors in the direction of egress.......
(e) activation of the building automatic sprinkler or fire detection system....shall automatically unlock the doors in the direction of egress....
So you see - those doors should NOT lock when there is a loss of power...in fact, that is a violation of the law.....
What I would do is make sure that building management is aware of this - and if they are not willing to address it, let me know and I will have a 'friend' look into it...yup...I know people in the Wis. Fire Service.....hehehe :ybatty:
Hope this makes you feel a little better - knowing there is something that can and should be done to fix the problem.....oh - and I have all the reference books right here at my desk - it is what I do for a living~ :eek2: